    Default HVAC Help

    Honeywell thermostat on downstairs unit is flashing “heat on” but nothing is coming out the vents. Any help?
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son

  2. #2
    Join Date
    Mar 2002
    Location
    Lexington County
    Posts
    5,230

    Default

    Battery need replacing in thermostat?
    No air at all coming out of the vents?
    Does the emergency heat strips work?
    Check breakers to the outside unit and air handler?


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Jan 2003
    Location
    Nichols SC
    Posts
    346

    Default

    Fan or starting capacitor

  4. #4
    Join Date
    Jan 2004
    Location
    Upstate, SC
    Posts
    1,077

    Default

    More info needed. Heat Pump w/electric strip or gas furnace?

    As mentioned above, check breakers first.
    Switch on AC and see if your fan works. Could be a capacitor issue.

  5. #5
    Join Date
    Nov 2009
    Location
    Spartanburg
    Posts
    1,690

    Default

    Out of propane

  6. #6
    Join Date
    Dec 2006
    Location
    Gray Court, SC
    Posts
    2,042

    Default

    Electric heat. Outside unit is not working. Jumped the red and yellow behind the thermostat and outside unit still doesn’t start. Jumped the red and green and the blower comes on and air comes out of vents. Thinking the capacitor at the outside unit?
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son

  7. #7
    Join Date
    Aug 2013
    Posts
    3,316

    Default

    See if fan will run by helping it start to turn.

  8. #8
    Join Date
    Jan 2008
    Location
    Monticello, AR
    Posts
    1,946

    Default

    Quote Originally Posted by CantCareSB View Post
    Electric heat. Outside unit is not working. Jumped the red and yellow behind the thermostat and outside unit still doesn’t start. Jumped the red and green and the blower comes on and air comes out of vents. Thinking the capacitor at the outside unit?
    That’s a good place to start. Sounds like what happened when the capacitor went out on my parent’s unit.
    For the ducks

  9. #9
    Join Date
    Dec 2015
    Location
    Six Mile SC
    Posts
    518

    Default

    What model Honeywell stat ? If it’s a newer one on a heatpump when heating or cooling on is flashing it is in delay. When it’s on solid (no flash) then equipment should be on.

  10. #10
    Join Date
    Dec 2006
    Location
    Gray Court, SC
    Posts
    2,042

    Default

    This is the thermostat https://www.supplyhouse.com/Honeywel...hite-4089000-p

    Finally got a chance to go outside and pull the panel off now that the wife is home. Pushed the contact and the outside unit fired up like it supposed to, so not the capacitor. My guess now would be the board. Outside unit is a Lennox 14HPX-024-230-10
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son

  11. #11
    Join Date
    Dec 2015
    Location
    Six Mile SC
    Posts
    518

    Default

    Quote Originally Posted by CantCareSB View Post
    This is the thermostat https://www.supplyhouse.com/Honeywel...hite-4089000-p

    Finally got a chance to go outside and pull the panel off now that the wife is home. Pushed the contact and the outside unit fired up like it supposed to, so not the capacitor. My guess now would be the board. Outside unit is a Lennox 14HPX-024-230-10
    If it is flashing heat on it is in delay. If it’s a heatpump that delay is 5 minutes. When you are sitting there waiting on one 5 mins seems like an eternity. That delay is in there to protect the compressor. BJ.

  12. #12
    Join Date
    Dec 2006
    Location
    Gray Court, SC
    Posts
    2,042

    Default

    It sat there for well over 30 min before I turned the thermostat off. Turn cool on an the fan blows inside but outside won’t
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son

  13. #13
    Join Date
    Dec 2015
    Location
    Six Mile SC
    Posts
    518

    Default

    Quote Originally Posted by CantCareSB View Post
    It sat there for well over 30 min before I turned the thermostat off. Turn cool on an the fan blows inside but outside won’t
    Not saying you don’t have an issue with the unit. But the flash is a built in delay. If it flashes for 5 mins, clicks to bring on system and goes back to flashing that is normally indicative of a low voltage short.

  14. #14
    Join Date
    Dec 2006
    Location
    Gray Court, SC
    Posts
    2,042

    Default

    Thanks. Where should I start looking then?
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son

  15. #15
    Join Date
    Nov 2017
    Posts
    42

    Default

    Sounds like you are not getting your 24 volts to the outside unit. If you can press the contractor and the unit comes on.

  16. #16
    Join Date
    Aug 2009
    Location
    PeeDee
    Posts
    8,582

    Default

    Did you have a storm in the last two days? Sounds like a problem I had with my unit. One of the wires leading back to my Thermostat fried. Swapped to another wire and it worked like a charm.

  17. #17
    Join Date
    Dec 2006
    Location
    Gray Court, SC
    Posts
    2,042

    Default

    Quote Originally Posted by XHailGC View Post
    Did you have a storm in the last two days? Sounds like a problem I had with my unit. One of the wires leading back to my Thermostat fried. Swapped to another wire and it worked like a charm.
    No storms lately
    "If its better than cold beer and hot pussy it'll probably kill us all" ~ Rebel Son